Coppersmith
Senior Member
- Location
- Tampa, FL, USA
- Occupation
- Electrical Contractor
An inspector rejected an installation of a mini-split a/c system because the control cable between the compressor and the head was not in a raceway. He sited 326.16 (which doesn't exist in 2014) and said it wasn't in a raceway. He probably meant 336.12(2). The part that is exposed is about three feet before it goes into a "trough" (not an electrical trough) along with the refrigerate lines. It's zip-tied to the lines. This is the standard installation and has never been flagged by an inspector before.
Q1: Is that cable a type TC? (It's four conductor, low voltage, doesn't seem to be marked.)
Q2: Would sleeving it in liquidtite until it gets inside the trough sufficient? Or does it need to be in a raceway all the way to the head unit?