problem is that you have two problems most of the times at inspections I have dealt with, first is circuit is dead, so can only use nominal voltage and distance to calculate voltage drop, and second is normally unless you are actually installing a machine you just have an outlet there at one end and a breaker at the other..
C405.9 Voltage Drop in Feeders and Branch Circuits
The total voltage drop across the combination of feeders and branch circuits shall not exceed 5 percent.
The code doesn’t say calculated voltage drop. It says voltage drop. Which means actual voltage drop
Now, to me it seems pretty simple to use voltage drop as part of my calculations for the proper cable sizing. I mean the formula is not that hard and, if I remember from last time I did it, the inverse of the voltage drop formula can pretty much give you the cable size.. You only need to know are you using copper or aluminum, and is it single phase or three phase, and use a good calculator.. Had the formula somewhere- think it is like 2KID/circular mils..