iggy2
Senior Member
- Location
- NEw England
We are working on 2 electric service equipment replacements, rated 1,200 and 1,600 amperes. The billed maximum demands over 12 months are 245 and 252 kVA (680 and 700 amperes). The ceiling height in the basements where the switchgear is located is 90", so typical gear will not fit, even if set on the floor, much less on a pad.
Is it reasonable to propose to the AHJ that the replacement equipment be rated less than existing, say 800 amperes, based on the 12 month max demand? See 220.87 which would allow me to use the max demand for additions to the service; but it does not address sizing of a service based on measured demand...
Is it reasonable to propose to the AHJ that the replacement equipment be rated less than existing, say 800 amperes, based on the 12 month max demand? See 220.87 which would allow me to use the max demand for additions to the service; but it does not address sizing of a service based on measured demand...