I'm working on a job that is an existing industrial plant (circa 1950) converted to offices. There is an existing 120/208V wye bus duct running throught the plant that we'd like to reuse. The nameplate says "1350A, 600 volts or less, 3 PH-4W, neutral capacity 675A (337A per bar, 2 bars)."
The original distribution system was demolished. A different engineering firm designed to feed this duct with a 1200A circuit breaker. I am extending a circuit from this buss duct to a 1200A distribution panel. Obviously, I am concerned about the undersized neutral (675A/1200A=56%).
The only code section I could find is 220.61 (2008) for calculating the feeder neutral. It says size the neutral per "The maximum unbalanced load shall be the maximum net calculated load between the neutral and any one ungrounded conductor". This confuses me since the 3-phase loads should have 0 neutral current. Also, at 1200A that's a lot of circuits to track down and try to figure out the actual neutral load.
My plan is to discuss the issue with the engineer that did the "line side" design and possibly reduce the feeder breaker from 1200A to 800A, similarly, reduce my "load side" distribution panel to 800A. Then the system would have an 84% neutral as opposed to a 56%.
Any thoughts?
The original distribution system was demolished. A different engineering firm designed to feed this duct with a 1200A circuit breaker. I am extending a circuit from this buss duct to a 1200A distribution panel. Obviously, I am concerned about the undersized neutral (675A/1200A=56%).
The only code section I could find is 220.61 (2008) for calculating the feeder neutral. It says size the neutral per "The maximum unbalanced load shall be the maximum net calculated load between the neutral and any one ungrounded conductor". This confuses me since the 3-phase loads should have 0 neutral current. Also, at 1200A that's a lot of circuits to track down and try to figure out the actual neutral load.
My plan is to discuss the issue with the engineer that did the "line side" design and possibly reduce the feeder breaker from 1200A to 800A, similarly, reduce my "load side" distribution panel to 800A. Then the system would have an 84% neutral as opposed to a 56%.
Any thoughts?