I have 16 post lights evenly spaced on a 1000ft. run. The lights are 180 watts each on a two-pole multiwire branch circuit. I have 8 lights on each pole of the 2-pole 20 amp gfi breaker. I am using #2 aluminum USE cable to prevent unacceptable voltage drop. My question is since the load is balanced is it acceptable to use a reduced neutral such as a size 2-2-4 w/6gnd. cable. I couldn't find my situation in the code book.
 
I am assuming these are 120 volt fixtures. This being the case I don't think you can share the neutral on a GFI circuit. It won't work. Again if it is 120 volts than why would you undersize the neutral??
 
You could reduce the neutral, it need be only large enough to handle the maximum imbalance.

Considering you are balancing the circuit the neutral will not carry any current until a lamp burns out.

A couple of points.

I would alternate the circuits.

I would forget the GFCI, as much as I like GFCIs it will likely be a nuisance and will not have much benefit.

You will need to run an EGC as large as your line conductors due to 250.122(B)
 
Dennis Alwon said:
I am assuming these are 120 volt fixtures. This being the case I don't think you can share the neutral on a GFI circuit. It won't work.

With a two pole GFCI this can work.
 
iwire said:
You could reduce the neutral, it need be only large enough to handle the maximum imbalance.

Considering you are balancing the circuit the neutral will not carry any current until a lamp burns out.

A couple of points.

I would alternate the circuits.

I would forget the GFCI, as much as I like GFCIs it will likely be a nuisance and will not have much benefit.

You will need to run an EGC as large as your line conductors due to 250.122(B)

You need to increase the EGC proportionately to the ungrounded conductors.

Tom
 
But what about 250.122-C? Where a single equipment grounding conductor is run with multiple circuits in the same raceway or cable, it shall be sized for the largest overcurrent device protecting conductors in the raceway or cable.
 
Table 250. 122?


15A 14cu 12al
20A 12cu 10al
30A 10cu 8al

Am I missing something, I'm not trying to be a pain. I took proportionately in terms of the circular mil of the ungrounded conductors. I guess it's so. But how about 250. 122 (C)? in this application. Or do we apply the 250.122(B) only? Or in addition to (C), now I'm confused.

Circuits of 15,20,30A are not neccesarily run in 14,12,10ga wire.

Tom
 
sparky59 said:
But what about 250.122-C? Where a single equipment grounding conductor is run with multiple circuits in the same raceway or cable, it shall be sized for the largest overcurrent device protecting conductors in the raceway or cable.

That still does not alleviate you from the requirements of 250.122(B).

Besides, code wise you have one multiwire branch circuit.
 
Davis9 said:
I took proportionately in terms of the circular mil of the ungrounded conductors. I guess it's so.

It is so. ;)


Circuits of 15,20,30A are not neccesarily run in 14,12,10ga wire.

Tell me about it.

We spend a lot of our time wiring site lighting at malls, stores.

You can find us running 4 AWG CU circuit conductors with 4 AWG CU EGCs.
 
Tom, we would have to use 250.122(B)

(B) Increased in Size Where ungrounded conductors are increased in size, equipment grounding conductors, where installed, shall be increased in size proportionately according to circular mil area of the ungrounded conductors.

This would mean if you increased a 20 amp circuit's ungrounded conductor to a #3 for VD the EGC would have to be a #3 also.

In reality the article needs some refining but as it stands right now 15,20,and 30 amp circuits must be 1-1

Roger
 
I hear you, it's a good thing you asked, although I wonder sometimes. If the EGC is OK for 100A is it overkill?


Tom
 
The reason for oversizing the conductors is voltage drop, which is caused by the resistance of the wire itself. If you don't increase the size of the egc, the same resitance (of the wire itself) will reduce the fault current. It's no longer a "low impedance path"
I think I understand this better than I explain it:rolleyes: , so if someone can jump in and explain it better, please do!
 