According to B.310.15(B)(2)(7) 750MCM AL is 425A for RHO 90 and LF 100 .
Assuming that You need to match the ampacity once you are out of the duct bank.
500MCM AL will get you 426.8A at 104 deg F as long as you can get the free air rating for say at least last 10 ft of the run. (350 MCM CU would provide 444.4A )
If the actual load is less (which seem to be likely) you can get away with less.
There is a free software “Conductor Ampacity Calculator“ at
https://www.mc-group.ca/software_downloads.htm that can help you find the right configuration of wires taking in to account ambient temperature. Although I would start with RFI about the calculated load – maybe the guy who pays for all of this could get you some answers.