redundant grounds in patient care facility

Status
Not open for further replies.

ecockrell

Member
Location
New Orleans
Found where conductors were run in PVC conduit underground to patient care areas. 517.13 A requires conductors to be installed in a conduit that is approved as a equipment grounding path as noted in 250.118. In leu of the fact that the clinic is open for business, would the idea of installing a #6 ground wire from the panel and tapping off of each of the conduits with a #10 wire and a pipe clamp be acceptable.
Thanks in advance for your answer.
Ed
 
In leu of the fact that the clinic is open for business, would the idea of installing a #6 ground wire from the panel and tapping off of each of the conduits with a #10 wire and a pipe clamp be acceptable.

I'm not sure that I understand your description, but it sounds like you do not comply with the requirement that conduit be a ground path. If this is true, the only one who's opinion really matters is the AHJ.

You might want to contact them.

Jim T
 
The short answer is no. Installing a second "wire" conductor does not acheive the "raceway as an Equipment Grounding Conductor" requirement.

You may be able to pull a type HCFC cable through the PVC.

Roger
 
You may be able to pull a type HCFC cable through the PVC.

I used to specify hospital grade AC cable in a pvc sleeve in the slab, until an inspector pointed out that the conduit is a wet location. The cable that I was specifying was not listed for use in a wet location.

Is HCFC listed for use in a wet location?

Jim T
 
Jim, I agree.

It looks like the OP will need to find a different route for new conduit in order to be code compliant.

Roger
 
jtester said:
Is HCFC listed for use in a wet location?

I think the answer is no. AFC's HCF-90 uses THHN conductors and they only list it at 90deg.C (dry)

Others may have THHN/THWN conductors. Not sure.
 