Reforming Capacitors on VFDs after Storage
Saturn_Europa
Fishing Industry
Electrician Limited License NC, QMED Electrician
The plant I work at, had a 200 HP VFD Powerflex 750 make a loud bang then trip a 400 amp breaker. I replaced the VFD with one we had in storage. Not sure how long it has been on the shelf but at least 3 years. I searched through the manual and did not see anything about reforming the capacitors, so I decided to apply power (480v) and wait a few hours before applying a load. This is the method listed for the Automation Direct VFDs we normally use.
I did some more searching and found this Allen Bradley service bulletin:
Table 3 - Drive Storage Duration and Reforming Recommendations.Duration Reforming GuidelineUnder 2 years No reforming required.
2 …3 years Apply rated voltage, per the normal method, for 30 minutes under no load.
Over 3 years Using a DC power supply connected directly to the DC terminals of the product, ramp-up the voltage from 0…100% of DC bus voltage (as per Table 4) in increments of 50%, 75%, and 100% rated voltage, under no load, for 30 minutes at each increment. See Figure 5 on page 4 for an illustration of this method
Does anyone actually use the last method? I dont have this type of equipment and would have to hire someone to reform the caps.
This drive costs over $21k. Does not reforming the capacitors properly effect the longevity of the VFD? Or is it only a danger of capacitor failure on startup?
Hopefully the instructions also include how to isolate the bus discharge resistor when using the direct DC application method. Not doing that can result in... interesting times (ask me how I know ;) )
I'd guess I could take it to a motor/drive repair place and have them do this for much less than $21k? May be more cost if I bring it in and tell them I need it yesterday than for them to do at their convenience though.
IIRC
Sqrt of 2 * 480 = 679
Yeah, but they were never quite that high, even when the motors were idle. No idea why, though. The cap tester one of the guys and I built would push up to about 710 using 120V input ( input - variac - backfed 480:120 transformer - DC rectifier - DC bus)
How old are the caps in the first place? Rather than reforming, it might be easier (and give everyone some peace of mind) to just recap and be done with it.
The op part reformed capacitor and vfd working. He to convince plant management for replace seemingly well working vfd capacitor
The issue is not "longevity", it is a lot more immediate in nature. If the capacitors have already de-formed (more below), just applying full voltage to the line terminals will blow the caps apart, often violently to the point of taking out other things in the drive. I had one blow the doors off of a 40HP drive once., it's pretty spectacular (unless you have to pay the bills). The issue is that the way electrolytic caps work, these are layers of aluminum film line foil, inside with an electrolyte gel in between them. When first made, a current is passed through the film layers and a layer of aluminum oxide, an insulator, forms on the surface of each layer. That insulating layer is what makes it a capacitor. When sitting unpowered for a long time, some of that aluminum oxide dissolves back into the electrolyte and the layer gets thin, then cracks, referred to as the oxide layer "de-forming" (because it was "formed" in the first place). If full voltage is applied, those cracks allow full current to jump the gaps between layers and burn holes in them, destroying them and often simultaneously vaporizing the electrolyte, which is what make it explode. By applying LOW VOTAGE DC to the caps and keeping the current below 1/2A (500mA) however, the same process that MADE it a cap in the first place, the growing or "re-forming" of that aluminum oxide layer, takes place, so the capacitor self-heals by "sealing" the cracks in the layer and is returned to normal operation. That cannot be rushed, because it is a "growing" process. If you simply energize a stored drive every so often (I've always used once per year, A-B says 2 years), any small cracks that STARTED to form will self-heal before they can become destructive.
The re-forming process differs for different manufacturers based on the construction of the drive, you really can't compare one to another. Also the time frame for when it is necessary tends to vary as well, even within the same manufacturer. I have another document from Rockwell that is close, but not the same, as what you read :
Disconnect the Drives control boards and I/O boards prior to applying the DC voltage. Otherwise, the external
power supply will turn on the Drive, and in the process draw too much current and overload the supply.
< 1 year and stored at rated temperature and humidity conditions (No reforming required)
1 – 2 years: Apply rated voltage, per the normal method, for 60 minutes under no load.
2 – 3 years: Using a DC power supply connected directly to the DC terminals of the product, ramp-up voltage
from 0-100% of DC bus voltage (see table below) in steps of 25%. Dwell at 25%, 50% and 75% steps for 30
minutes each. At 100% voltage, dwell for 60 minutes, all under no load.
from 0-100% of DC bus voltage (see table below) in steps of 25%. Dwell at each step for 120 minutes
The final forming voltage shall be 1.35 – 1.45 times the rated AC system voltage
Power supply current draw must not exceed 500 mA.
You CAN, by the way, connect the DC to the DC terminals of the VFD if it has them, but they still want you to unplug any control boards on the larger drives (PF700 / 750). Some people say it's OK to apply power to the AC line terminals through a variac (variable transformer), and I have done that many times, but in some drives, doing so is also then giving low voltage to the control system for the drive and can damage some of them, so it's kind of a craps shoot. The trick there though is to use a current meter with it and adjust the AC to ensure that the current flow is never more than 500mA. (Edit: I have built my own capacitor re-former for this with a 120V variac, a current limiting resistor, a 1A ammeter and a CPT that steps the 120V to 240 or 480 as the case may be, and 1/2A fuses on the HV side.)
I have had several people tell me that they just hook up some light bulbs in series to the AC terminals to drop the voltage to the drive, then unscrew bulbs one at a time over a few hours to increase the voltage. I don't recommend this method as it is a lot less accurate, and I have seen one of these setups fail to protect the drive, so they lost it anyway.
The Baldor drives I worked on (15H and 18H) back in the early '00s would be ~655VDC for a 480VAC input.
On the many Danfoss & ABB drives that I PM'ed ,troubleshoot, installed & replaced the DC Buss for 480 volt three phase was 660 to 670 volts DC . Older drives were a few volts less. Believe it's the RMS multiplier of 1.414 ( 480 × 1.414 = 678.72 volts DC ). Even when I had 485 to 490 volts input at a drive never seemed to ever have a DC Buss voltage above 670 volts. A few times when I attempted to start a 40 to 75 HP return fan that was in a AHU that had two 75 to 125 HP supply fans both running over 40 Hertz ( 66% of full speed ) would have over 750 DC buss voltage on return fan drive because the return fan was running fairly fast in reverse and drive could not perform a flying start.On 18 pulse drives I had one with a 40 HP return fan that never ran more then 60% of full speed only showing a DC Buss voltage below think.it was 460 volts DC because one of the two inputs was bad. It was for an important space and they never gave me the permission to shut it down to fully troubleshoot. Also had regular drive return fan had one blown fuse ( luckily the one that did not supply power supply ) that was running around 60% of full speed that ran okay for hours until after department was done for the day then I was able to replace the blown fuse. That also had a reduced DC Buss voltage. Set the maximum speed to 40 Hertz to prevent it from attempting to run at a faster speed then reduced DC Buss would allow.