We are wiring a new grocery store and they have a refrigeration (cold case) unit that has a label with this info:
115v
1 phase
13.0 refrig cycle
locked rotor 46.0
I have never had to deal with locked rotor rating and does this play in at all on conductor/ocp sizing. Right now we are feeding this unit with #12's and a 20 amp breaker with meets the requirements I have read in the code. Any input or are we doing this right?