Refrigeration Load

Status
Not open for further replies.
Well, since the sentence specifically mentions the table and then overrides the result of using the table, it seems pretty clear that is what is intended. :)
The fact that the table provides different answers for different situations does not affect the fact that the whole table process is being overridden IF the result from the table is larger than the rest of the circuit conductors.
Note that if the circuit conductors include a reduced size neutral, this does not allow you to just use the size of the neutral! The limit would be the largest of the circuit conductors.

Ok...I get it. I understand now. Thanks.
 