- Massachusetts
Fridge in the garage? Where's the violation?
Who said it is in the garage?
Please note that the NEC (210) simply discussed refrigerators that happen to be located in the kitchen. Nowhere does the NEC say that all refrigerators MUST be in the kitchen.
The OP also needs to be reminded that new fridges should work fine on a GFCI. If the fridge is tripping the GFCI, it's time to replace the fridge.
Wow, step away for a day and look at you guys.![]()
Worst case scenario I will fix the problem for him at no cost. One of the kitchen gfi's is right next to the fridge and it wouldn't take much to add one behind the fridge on the line side of that gfi.
Side note: I can see an inspector easily missing this if the garage was on the load side of the GFCI, but not if the fridge is on the load side of the garage.
Most likely though, he tripped the counter GFCIs and only checked the receps that might have been on the load side of them, then didn't check the fridge assuming it was also on the load from the counter.
Or maybe the panel is marked fridge and he flipped the breaker and it worked the recep at the fridge and didn't notice it also worked the garage.
He probably just tripped the GFCI in the garage to check it.
Just MPO, but either way, he totally missed the boat on it.
If nothing is plugged into the garage GFCI receptacle the refrig is on a 15 amp circuit by itself. Adding a new refrig receptacle by connecting it to an existing SABC isn't much better than what you have now.
Maybe it's me but this doesn't seem like a great solution. If nothing is plugged into the garage GFCI receptacle the refrig is on a 15 amp circuit by itself. Adding a new refrig receptacle by connecting it to an existing SABC isn't much better than what you have now.
If the house is only a month old, I see no reason what-so-ever that you should fix the problem on your dime. Even if you are trying to build a relationship with the HO. You are trying to help them rectify the problem and that should be enough to let them know you are on their side.
...Worst case scenario I will fix the problem for him at no cost. One of the kitchen gfi's is right next to the fridge and it wouldn't take much to add one behind the fridge on the line side of that gfi.
And yet not one person suggested that you could just come off of the line side of the GFCI. Either on the SABC or the garage.
How can the kitchen refrigerator be on a 15 amp circuit with the garage receptacle?
Actually, I did.![]()
A kitchen refrigerator is required to be on either a SABC or if it's a 15 amp circuit then it must be a individual branch circuit. I don't see how switching it to the line side of the garage GFCI will make it code compliant.