Regarding 682.33:equipotential grounding plane

Status
Not open for further replies.

wyboy

Senior Member
Regarding NEC 682.33: It is my understanding that only the disconnect or service need an equipotential grounding plane- not the motor controller or any other equipment on the load side of the disconnect. Is this correct?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Regarding NEC 682.33: It is my understanding that only the disconnect or service need an equipotential grounding plane- not the motor controller or any other equipment on the load side of the disconnect. Is this correct?
The EPG has nothing to do with the circuits of a pool. This is a bond wire that usually bonds together all metal in the pool , walkways, rebar etc and all metallic parts associated with the pool, It does not get connected to any circuit conductors or EGC.
 