Reidentification of conductors

Status
Not open for further replies.

joebell

Senior Member
Location
New Hampshire
I was asked today if it is ok to reidentify a blue conductor to white in a 12/4 MC cable and use it as a grounded conductor. My first instinct was no 200.6(A) would not allow this but instead of stopping there I continued reading and read 200.6(E) ex1. This pretty much allows the installation above regardless of wire size.

Am I reading this right?
 
Smaller than #8 has to be identified from end to end.

Thats not the way I am reading this. I agree 200.6(A) limits the size of the conductor but I don't think 200.6(E) ex1 does.

That only applies where only qualified persons service the installation.

Couild you explain this, If the circuits originate from a panel in a locked electrical closet and feed office furniture partitions would this qualify?
 
Couild you explain this, If the circuits originate from a panel in a locked electrical closet and feed office furniture partitions would this qualify?


This exception usually applies to plants and places with their own maintaince electricians.
 
This exception usually applies to plants and places with their own maintaince electricians.

This building is the headquaters for a major athletic shoe company(office building). They do have there own maintaince staff but does this qualify? I'm thinking maybe not.
 