dhducati
Member
- Location
- Pennsylvania
I was wondering about using some left-over black #4 THHN to bond a water line to the service panel (200A service). Parts of the run through a crawl space will be exposed. 250.119 allows re-identification, but in this case there would be relatively long lengths where the conductor is accessible. Would the whole accessible length need to be taped green? Perhaps it would be easier to use bare wire, or get some green #4 and save the left-over black for another job.