Strathead
Senior Member
- Location
- Ocala, Florida, USA
- Occupation
- Electrician/Estimator/Project Manager/Superintendent
Can you back that up with a manufacturer's recommendation? I would assume either the wire or the lug manufacturer would publish this if it is an issue. Otherwise, there would be nothing "wrong" with reterminating. I am not trying to be argumentative here. I have never contemplated this issue and I want to log it in the back of my mind for future consideration.The original termination has already crushed the conductor and it should not be re-terminated without trimming it back. The original torque specifications accounts for the cold flow that will occur over time as the pressure extrudes the conductor out from under the screw. There is no way to account for that when you re-terminate it as that cold flow happened with the original termination.