I look for any empirical relationship between the maximum demand of an installation and size of a diesel generator to serve it.
Incidentally, I calculated the MD of a building based on connected loads and applicable diversity factors for sizing up a diesel generator per official guidelines. The maximum demand worked out to be 100 KVA. So the size of the diesel generator may also be taken to be 100 KVA. But per the digital energy meter of the building the recorded MD is around 30 KVA only. So which value will serve as correct size for the Diesel generator to be selected ? Thanks.
Incidentally, I calculated the MD of a building based on connected loads and applicable diversity factors for sizing up a diesel generator per official guidelines. The maximum demand worked out to be 100 KVA. So the size of the diesel generator may also be taken to be 100 KVA. But per the digital energy meter of the building the recorded MD is around 30 KVA only. So which value will serve as correct size for the Diesel generator to be selected ? Thanks.