when looking at the drawing on a relay is it shown in the energized or de-energized position?
whatever powers the coil is what turns it on and off. So if your relay coil is 120 volts then you wouldn't want it constantly on or else there wouldn't be much need for the relay. When the coil is energized then the N.O. contacts close and the N.C. contacts open and when the coil is de-energized then the contacts do the opposite or return to their normal state.Thanks for the replys. The reason I ask is because i dont have much motor control experience so i am taking a motor control class and there is a few things I dont understand. When you feed the relay with your 120v does that have to be constant or do you switch that 120v on and off to control the relay? I can see where pin 5 and 6 are used for actuating so that makes me think that the 120v should be constant comin in on terminal 2
I'm not quite following what you say.thats what had me confused. This is a time delay relay. I have my 120v feeding my relay and my trigger switch. I also have constant 120v feeding one side of my NO contacts and the other side goes to my contactor to provide a off delay for the contactor when the relay is closed. My question is does the other side of my trigger switch need to jump to anything else or do i have this right?![]()
If it is the time delay relay that I am thinking of, you close a contact between terminals 5 and 6 to trigger the timer.
They are usually shown in thier normal state, that could be energized or denergized, open or closed, etc...what ever is the normal state.
Not always.
Seen 'em both ways... and I'd say the de-energized contacts type of schematics are prevalent.
That is why I didnt say always. And I agree with you about the de-energized being the norm, nut what about a UV coil for example?
I especially hate "a 3-position switch with (1) normally open and (1) normally closed contacts.I tend to cringe, when I hear the terms "normally open" or "normally closed," both in the context of switches and in the context of relay contacts. These phrases provide such great opportunities for mis-interpretation.
Every diagram I have worked with has shown the shelf (de-energized) state of all relays (UV coils not excepted). It does not matter whether the relay, when in its "usual" (note that I did not say "normal") operating condition, has power all the time.
I tend to cringe, when I hear the terms "normally open" or "normally closed," both in the context of switches and in the context of relay contacts. These phrases provide such great opportunities for mis-interpretation. I prefer the convention that in the shelf state of a relay, its "a contacts" are open and its "b contacts" are closed. Thus, when I look at a control diagram, and I see an "a contact," and if I determine that that relay will have power most of its operating life, I will infer that that "a contact" will be closed for most of its operating life. That is the mind set I have when study such diagrams.