I have a corridor going to an electric room and mechanical room like in the picture I attached. The corridor comes opens to another corridor.

Where do I need RAIs? Do they need to be outside the corridor as well as the mechanical and electric rooms? I can't find in the fire alarm code where it references this.
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
View attachment 8097
I have a corridor going to an electric room and mechanical room like in the picture I attached. The corridor comes opens to another corridor.

Where do I need RAIs? Do they need to be outside the corridor as well as the mechanical and electric rooms? I can't find in the fire alarm code where it references this.

Try 18.5.5.5 NFPA 72
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
View attachment 8097
I have a corridor going to an electric room and mechanical room like in the picture I attached. The corridor comes opens to another corridor.

Where do I need RAIs? Do they need to be outside the corridor as well as the mechanical and electric rooms? I can't find in the fire alarm code where it references this.

We're on the 2007 edition of NFPA 72, and off the top of my head I don't recall a requirement for RAI's. This is usually a spec driven requirement. It's somewhat redundant with the advent of addressable panels.
 