To add to this discussion:
IEEE 142 (green book) Grounding of Industrial and Commercial Power Systems states the following reasons for system grounding.
1.3 Purposes of system grounding
System grounding is the intentional connection to ground of a phase or neutral conductor
for the purpose of:
a) Controlling the voltage with respect to earth, or ground, within predictable limits,
and
b) Providing for a flow of current that will allow detection of an unwanted
connection between system conductors and ground. Such detection may then
initiate operation of automatic devices to remove the source of voltage from these
conductors.
The NEC prescribes certain system grounding connections that must be made to be in
compliance with the code. The control of voltage to ground limits the voltage stress on the
insulation of conductors so that insulation performance can more readily be predicted. The
control of voltage also allows reduction of shock hazard to persons who might come in
contact with live conductors.
for the purpose of:
and
conductors.