The inspector is wrong. This is not allowed. Presumably the low voltage is fed from a Class 2 power supply for this application. You cannot mix power and class 2 signaling conductors despite them having the same type of insulation. I am unable to provide a reference as I don't have my book with me but someone else will know it.Originally posted by bigjohn67:
BTW.... The inspector passed this installation ...
He stated that different derived systems were allowed in the same conduit as long as they were identified.
725.52(A)Exception No. 2: Class 2 and Class 3 circuits shall be permitted to be reclassified and installed as Class 1 circuits if the Class 2 and Class 3 markings required in 725.42 are eliminated and the entire circuit is installed using the wiring methods and materials in accordance with Part II, Class 1 circuits. Class 2 and Class 3 circuits reclassified and installed as Class 1 circuits shall not be classified as Class 2 or Class 3 circuits, regardless of the continued connection to a Class 2 or Class 3 power source.
What's the problem? Simple, you are violating the code.Originally posted by bigjohn67:
Peterd
1. I never once mentioned anything about the same insulation on the wire.
2. Although the voltage is different (120 and 12) they are both A/C voltage. The control wires are nothing more than a 2 wire return (12v A/C)Again, I never said this wire is a signal wire.
3. The control voltage is stepped down within the gate controller. So if you turn off the 120v you will loose the 12v also.
So Whats the problem? But I guess I should "give the code more than a passing glance and dig into it a lot deeper."