The issue is probably not running load with the meter bypassed, but cutting the seal to gain access to the bypass. Personally, as a POCO guy, I was never a fan of lever bypass meters. Biggest problem was if you wanted to de-energize the line side jaws. More than one utility besides ours has requirements that state that a meter shall not be installed or removed when the socket is energized (usually on 277/480 services). May be overkill, but it is as a result of arc flash injuries when a meter is installed or pulled in an energized socket and a fault occurs. Lots of gory pics at our safety meetings. Requirements are now that the test/bypass disconnect link must be open (which de-energizes line and load side jaws) when installing or removing a meter from a bypass type meter panel. Called a test/bypass type of meter enclosure. If anyone is unfamiliar with these, Google it if you care. That is not possible with a lever bypass meter. Some utilities have even gone so far as to forbid installing or removing a meter from any type socket while energized, which means a disconnect at the transformer. That is definitely overkill, in my opinion. One other issue is that lever bypass meter cans have ringless covers, meaning the cover must be removed before the meter can be removed. Some utilities feel that this increases the risk. Some utilities (ours and some other EUSERC member utilities) do not allow ringless sockets. We require the ability to install locking meter rings if we choose to. I know there will be flaming arrows regarding my opinion, but it's just that...my opinion. If yours is different, I'll patiently explain why you're wrong.:lol: I know this is way off the original topic, but I'm bored, so be kind. Merry Christmas.