Very good Wayne.:wink: What you can't do is "dead end" the pipe. If you install the grounding electrode conductor in a metalic conduit, the conduit has to be bonded to the cabinet and the grounding electrode. Or What Wayne said may work to if you used something like a bonding bushing.
I'm not disagreeing then nor am I now. I'm gonna repeat one more time what I said in the last post. If he was using that article to say I need a connector which more or less it does, then he should have also pushed the issue of a jumper which he did NOT. I completely understand what the article says and had I read and been as familiar with it then (TWO YEARS AGO) as I am now I would have. :roll:
All he wanted was a connector and neither the jman that told me to do it nor the inspector mentioned anything about a jumper so I let it go at that. (I was a 3rd year at the time) I let it go and didn't look it up until later I was wondering why the connector. Also the inspector didn't cite an article when he said that the pipe needs a connector because nobody questioned him.
Again the setup was pipe connected to panel, solid #6 I believe it was (might have been bigger I've slept a few times since then) through a 3/4 EMT out the wall connected to a ground clamp on the ground rod. I'm not misunderstanding anything. I'm not raising a fuss. I've read all of Article 250 many many many times since then believe, it was very prominent on my test as well. This has all gotten blown out of proportion over a simple comment.