kid_stevens
Senior Member
- Location
- Albuquerque, NM
I have been in several stores that had this kind of a problem. The breaker is now tripping so much that I worry about a fire. That is until I put a latching current meter on the circuit and see the breaker dropping out at 12amps or so. They have been cycled so many times due to a real overload that they moved the problem equipment to a different circuit to lighten the load. Well the old breaker is harmed by running at 20 or more Amps before it trips. Then it is reset while still hot and this weakens the breaker's sense circuit so much that it has no retention left. hundreds of these cycles in a year and the breaker is trashed.