zemingduan
Senior Member
- Location
- Philadelphia,PA
- Occupation
- Electrical Designer
We have a project that has an indoor unit substation dated back to 1973. The 13.2KV 3ph - 208Y/120V 3ph 500 KVA dry transformer of the unit substation is blown/ doesn't work according to the client.
The client want to just replace the core & coil of the transformer but reusing the existing enclosure. This is the name plate of the old transformer and the drawings of the new core & coil in stock.


The KVA, primary, secondary voltage ratings are the same. The impedance is a little bit different.
Is this allowed? Any concerns/issues? I thought the enclosure of the transformer is designed specifically by the manufacture for their specific core & coil. And I thought the transformer core & coil and the enclosure are listed as a whole assembly.
The drawings is only for the core & coil. It's note 6) states it meets DOE efficiency standards, and it lists the Temp rise as 150 C. Did they get the test data without the enclosure? Will different enclosures affect the efficiency, Temp rise, etc.... of the transformer since ventilation requirements may not be satisfied? And the highlighted texts only recommends instead of requires the enclosure vent opening area.
I need some knowledge and get educated here. Thank you!
The client want to just replace the core & coil of the transformer but reusing the existing enclosure. This is the name plate of the old transformer and the drawings of the new core & coil in stock.


The KVA, primary, secondary voltage ratings are the same. The impedance is a little bit different.
Is this allowed? Any concerns/issues? I thought the enclosure of the transformer is designed specifically by the manufacture for their specific core & coil. And I thought the transformer core & coil and the enclosure are listed as a whole assembly.
The drawings is only for the core & coil. It's note 6) states it meets DOE efficiency standards, and it lists the Temp rise as 150 C. Did they get the test data without the enclosure? Will different enclosures affect the efficiency, Temp rise, etc.... of the transformer since ventilation requirements may not be satisfied? And the highlighted texts only recommends instead of requires the enclosure vent opening area.
I need some knowledge and get educated here. Thank you!