paul said:I would contact the AHJ and see what they have to say about it.
cowboyjwc said:UAC Section 106: Whenever there are practical difficulties involved in carrying out the provisions of the technical codes, the building official may grant modifications for individual cases. The building official shall first find that a special individual reason makes the strict letter of the technical code impractical and the modification is in comformity with the intent and purpose of the technical code, and that such modification does not lessen health, life, safety and firesafety requirements or any degree of structural integrity. The details of actions granting modifications shall be recorded and entered in the files of the conde enforcement agency.
So can the AHJ over ride the code? Yes
Will they do it in this case? My guess is no.
By my estimation, I would say that replacing with a new panelboard is "new work" and must conform to the electrical code. Repairing would be a different scenario. :smile:MichaelJ said:Nec 240.24(d) states that overcurrent devices are not to be placed in clothes closets . Is there any exceptions to allow replacing a old fuse box with a new breaker panel and leave it in a closet? Thanks
I'll add a third part to your question. What's better: 1. Leave it as is; 2. Fix it so that it's slightly better but not legal; or 3. Make it code compliant.Jim W in Tampa said:Whats better,leave it as is or fix that is slightly better but not legal?
wbalsam1 said:I'll add a third part to your question. What's better: 1. Leave it as is; 2. Fix it so that it's slightly better but not legal; or 3. Make it code compliant.
Answer: #3 :smile:
Jim W in Tampa said:And if the owner can't afford number 3 then we would rather he keep #1 ?
We had a similar situation, large room,off of the bedroom, but it was just for shoes, Hummmmmm, No, It walks like a duck, it quacks like a duck, Hummm its probably a duck. No panel in the closet.Jim W in Tampa said:Whats better,leave it as is or fix that is slightly better but not legal?
its not that he is allowing a violation, as one post says, repairs are allowed to go back as origanally installed, but if the fuse box is going to be replaced because " i need more breaker space" that is a totaly differant situation. At least that is the way it is in the area where we work.Pierre C Belarge said:Jim
As you can see, once having been an inspector, it is not easy to say..."okay just this time" ...because it may come back and bite the inspector for permitting a violation for any reason.
Also, once one starts to give one person consideration for whatever, it is almost impossible to not start to give others some kind of consideration and then...well, why even have an inspector.
Jim W in Tampa said:............Sad part is that if it burns the insurance company will likely pay to bring it up to code............