Replacement feeder to detached garage

Status
Not open for further replies.

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Existing situation: 100 amp feeder made up of three (!) individual aluminum conductors exiting home panel through three separate 1/2" KOs (!!), in wall to crawl space, through foundation wall, multiple split-bolted splices under deck (!!!), buried to detached, steel-skin garage, up inside EMT to un-bonded panel (!!!!).

The neutral became intermittent, then open. There is grounding in the garage panel, but again, was never bonded to the neutral despite there being no EGC in the 3-wire feeder. I'm recommending that we abandon the existing conductors and run a new 4-wire feeder, rather than try to repair the existing neutral.

So, the question is: what wiring method would you use from panel, down inside the exterior wall into the crawl space, through the foundation wall, under the deck about 20 feet, in the ground about 10 feet, and up into the garage, probably with an LB through the skin if we can't easily re-use the existing EMT sleeve.
 
I would run SER from the panel to the crawl space. Then add a junction box and run conduit & THWN the rest of the way. Or you might use 100A mobile home wire from the JB if you can get it through the conduit without much trouble.
 