Hey guys,
I've never wired up one of these minisplit havac systems. I haven't been up to the roof yet to see the old unit and disconnect but I'm sure the disconnect needs replacing.
I traced out the old 240v branch circuit and it has (2) #10's going up to the roof to the disconnect from the panel for the compressor/condensor.
In a nutshell and listed in the link below: MCA = 31.9A / recommended breaker = 40A
Mitsubishi M series minisplit
I've never wired up one of these minisplit havac systems. I haven't been up to the roof yet to see the old unit and disconnect but I'm sure the disconnect needs replacing.
I traced out the old 240v branch circuit and it has (2) #10's going up to the roof to the disconnect from the panel for the compressor/condensor.
- When it comes to replacing the disconnect, can I just use a non-fused 60A disconnect up on the roof instead of a fused disconnect? Why you would want to use fused vs. non-fused?
In a nutshell and listed in the link below: MCA = 31.9A / recommended breaker = 40A
Mitsubishi M series minisplit