I dont think he's joking.I know you are joking, but all jokes aside, I picked up a box of 10 non TR for next to nothing 2 weeks ago.
I dont think he's joking.I know you are joking, but all jokes aside, I picked up a box of 10 non TR for next to nothing 2 weeks ago.
I'm pretty sure Chicago doesn't have a nickname for it.... My old boss called it the Boston wrap. I'm sure other areas of the country have their own nickname for it. ...
Yep, no shortage of non-TR receptacles around in stores.
My house was built in 1962 with 14/2 NM with the reduced #16 guage ground . Most of the what we called 2.5" bevel edge wall cases had a NM cable with one entering top of box & other bottom of box with maybe only 1" of wire wrapped around clamp screws. Wires are not long enough to splice together and had to make two splices inside small boxes. Was unable to use a crimp on fitting due to not able to get crimping tool into rear of box. They did use #12 NM cable on kitchen counter top receptacles.Yes.
Gem boxes.Most of the what we called 2.5" bevel edge wall cases had a NM cable with one entering top of box & other bottom of box with maybe only 1" of wire wrapped around clamp screws.
Aren't those the kind that break in half when you plug something in?I know you are joking, but all jokes aside, I picked up a box of 10 non TR for next to nothing 2 weeks ago
View attachment 2564273
Edit: But you can make them look old by letting the painter paint them after you install them
Been a couple times I've done the same thing. It was complaint to ground that way with the clamp screw at the time so I view it the same as adding an extension to a circuit with reduced ground size where what I add is properly sized to now even though it is fed from the 16 awg ground.Gem boxes.
I would have left the wires on the screws and added a jumper/pigtail.
You can from an ungrounded so long as your provide gfci so I can't think of a code reason it wouldn't be.Can you legally extend off a undersized egc? Without tapping into an appropriate sized egc. Forgot what section in 250 it’s staes we’re you can tap into
I understand your point it was compliant on install.
Can you legally extend off a undersized egc? Without tapping into an appropriate sized egc. Forgot what section in 250 it’s states we’re you can tap into
You can from an ungrounded so long as your provide gfci so I can't think of a code reason it wouldn't be.
That is exactly what he is saying. Yes, you can extend an existing grounded circuit with modern NM.zEdit: what confuses me is that if you can extend an ungrounded, then shouldn't you also be able to extend an undersized egc? Seems like that would be the safer extension of the two
Didn't like the idea of admitting I was lazy. I was remembering 210.12 (D) exception.lazy this morning
Note 406.4(D) requires replacement receptacles to be the Arc-Fault or Arc-Faulr protected if they are being installed in an area requiring AFCI per 21012(A) or (B)
I know there is a rule in the 2020 cycle talking about extending circuits without having to make the circuit compliant with current code.
Without getting out the code book, lazy this morning, I remember it limited the distance and you could only use splicing junction boxes. So I interpreted it as being written to allow you to relocate an exiting outlet without having to upgrade the whole circuit.
I don't know what any pre-2020 rules allow.