1. Some said even 4 feet is not nearest point of entry then if USE come up from underground conduit stuck up 1 feet , 2 feet,4 feet to switchboard same room that would be encased concrete too? . Thats not nearest point if entry
2. If AHJ has no rules and is ok with 4 feet then NEC 2014 code allows SE cable without conduit concealed within drywalls?
Residential townhomes meter and panelboard
I have residential townhomes. Each townhome is fed by its own electric utility service. I have utility meter outside the wall of the townhome and the main service with main circuit breaker panelboard is inside about four feet from the meter outside. The cable provided in between is SE cable...
forums.mikeholt.com
1. Some said even 4 feet is not nearest point of entry then if USE come up from underground conduit stuck up 1 feet , 2 feet,4 feet to switchboard same room that would be encased concrete too? . Thats not nearest point if entry
2. If AHJ has no rules and is ok with 4 feet then NEC 2014 code allows SE cable without conduit concealed within drywalls?