I'm not sure. I told her to call and find out so we can compare costs between that and installing a 6/3 copper.
I'm not sure. I told her to call and find out so we can compare costs between that and installing a 6/3 copper.
The chemicals to keep the spa chemistry correct cost 20x what a length of 6/2 costs (unless those were freebies too). and I dont want to know how the wiring from the disco to the tub is going to be done... sorry, but 680 installs are really not places to cut corners (not that anyplace really is, but especially not 680 installs).
I can guarantee you a visit from a spa tech to change the panelboard to 30A will cost more than the 6/2 or even 4/2 to wire it 60A, if that's where it's set at now; maybe ask her sister what the breaker sizes are/were for the spa at her place. btw, a spa of that age may very well have cracked plumbing fittings from age and chemicals, ofc you wont find out until you fill it and run all the pumps. Just moving the spa can cause them to snap/leak/crack.
Also, it is a good idea to go thru and check all the bonds in the pool panel to make sure they are there, tight, and not corroded. Last used spa I did had all of these problems (loose grounds, cracked fittings, set at 60A). Not saying you will but they are things to look at when installing a used spa.
Why Copper? Use some 6/3 or 4/3 AL. It will a heck of a lot cheaper (and quicker).
I thought that depending on which NEC is in force, and whether the SE cable is run through thermal insulation, that the ampacity may be determined from the 75C column, i.e. 50A.Since an 8/2 SE cable is rated at 40A
Nothing wrong with using that SE cable at all as long as the spa needs only 240 volts and not 120/240. You could use it for anything between 15 and 40 amp circuit. As mentioned it would not be allowed connected directly to the spa, but could terminate in the spa disconnect.If the manufacturer's service manual says that adjusting the board is a safe option for utilizing an existing circuit, is that considered cutting corners?
Since an 8/2 SE cable is rated at 40A, would protecting it with a 30A breaker be considered unsafe for a 680 install?
Please understand that I'm not trying to be sarcastic; I'm having a serious conversation.... Thanks!
If the manufacturer's service manual says that adjusting the board is a safe option for utilizing an existing circuit, is that considered cutting corners?
Since an 8/2 SE cable is rated at 40A, would protecting it with a 30A breaker be considered unsafe for a 680 install?
Please understand that I'm not trying to be sarcastic; I'm having a serious conversation.... Thanks!
I always use copper in all my installs. It easier for me to get my hands on, is a better conductor, and is more corrosion resistant (live near brackish water). The inspectors around here find it more favorable as well. It's just what i use I guess.
Try AL on jobs, it will save you $$$$ putting you above others. Weight for weight AL is actually many times better with conductivity. Most of what you here about AL is pure myth.
:thumbsup:
I substitute AL whenever possible. :happyyes:
I kind of presumed he wanted to put it on a 30 amp breaker because that is what the spa calls for. There are some out there that do only run on a 30 amp circuit, though you don't run into them very often. I have one that is considered a portable unit is big enough for 2 people, maybe 3 if they are not very big, and only has a 5-15 cord cap already on the unit. How they get away with that is it does not heat while running in high jet mode (user mode) pump runs at a low speed when heating.Also, running that spa at 30A imposes some operational limitations which may not be acceptable to the customer. Your friend may not mind, but every spa install Ive done, the customer would have been blowing up my phone had I installed wiring to it be only capable of 30A.
...
Sorry, the whole topic is a sore point as lots of spa owners spend 7k+ on a spa, 5k for the deck it sits on, then complain bitterly about a <1k electrical service to run it.