wrobotronic
Senior Member
- Location
- Colorado
Hi All,
Here is the scenario. Service coming in to line side of meter from the PoCo mounted to a standard pole. Load side of the meter has 3- 250 Al to a gutter. From said gutter 250's are tapped with #2 Al to feed a 60A barn panel (100' away) and tapped to 4/0 Al to a 200A panel on the house (100' in the other direction).
My concern is that I need to have a disco either between the load side of the meter and the gutter OR individual discos for each set of feeders leaving the gutter. I have ALWAYS set a means of disconnect for this type of setup. I usually opt for the individual disco scenario, so as to allow power to remain at one building or the other. But I also realize, that while this is convenient, it may not necessarily be required.
I have now been told that these discos are not required at the meter and the mains of each panel suffice. I was further told that if the feeders needed to be disconnected that pulling the meter was a sufficient way to do this.
So, am I wrong that each set of feeders needs to have a disco at the pole the service is mounted on? If these discos are, in fact, required, where in the good book does this exist?
TYIA.
Here is the scenario. Service coming in to line side of meter from the PoCo mounted to a standard pole. Load side of the meter has 3- 250 Al to a gutter. From said gutter 250's are tapped with #2 Al to feed a 60A barn panel (100' away) and tapped to 4/0 Al to a 200A panel on the house (100' in the other direction).
My concern is that I need to have a disco either between the load side of the meter and the gutter OR individual discos for each set of feeders leaving the gutter. I have ALWAYS set a means of disconnect for this type of setup. I usually opt for the individual disco scenario, so as to allow power to remain at one building or the other. But I also realize, that while this is convenient, it may not necessarily be required.
I have now been told that these discos are not required at the meter and the mains of each panel suffice. I was further told that if the feeders needed to be disconnected that pulling the meter was a sufficient way to do this.
So, am I wrong that each set of feeders needs to have a disco at the pole the service is mounted on? If these discos are, in fact, required, where in the good book does this exist?
TYIA.