wrobotronic
- Colorado
Hi All,
Here is the scenario. Service coming in to line side of meter from the PoCo mounted to a standard pole. Load side of the meter has 3- 250 Al to a gutter. From said gutter 250's are tapped with #2 Al to feed a 60A barn panel (100' away) and tapped to 4/0 Al to a 200A panel on the house (100' in the other direction).
My concern is that I need to have a disco either between the load side of the meter and the gutter OR individual discos for each set of feeders leaving the gutter. I have ALWAYS set a means of disconnect for this type of setup. I usually opt for the individual disco scenario, so as to allow power to remain at one building or the other. But I also realize, that while this is convenient, it may not necessarily be required.
I have now been told that these discos are not required at the meter and the mains of each panel suffice. I was further told that if the feeders needed to be disconnected that pulling the meter was a sufficient way to do this.
So, am I wrong that each set of feeders needs to have a disco at the pole the service is mounted on? If these discos are, in fact, required, where in the good book does this exist?
TYIA.
TYIA.