We are installing an 800 amp 3 phase 208v custom panel board for a machine shop which we have totally engineered in the field. This is being installed on the back side of an existing 1200 amp service and my drawings have been approved by the county.
My drawings indicate 3 -400 mcm alu - ungrounded and 1- 400 mcm grounded paralleled X 3.
The only neutral load is the existing 200 amp 3 phase lighting panel which now will be re fed from the new panel board.
Am I actually required to drag a neutral over for each set or can I go with 1 or 2?
Do I have to rate the neutral for the entire 800 amp service with such a small neutral load?