Requirements for wire nuts inside rooftop junction box

photonboy

Member
Location
Berkeley, CA, USA
Occupation
Ex roof monkey, current desk jockey
Are all wire nuts in a roof j-box required to be waterpoof? Trying to find a code section specifically referencing this but no luck so far.

Thanks.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Are all wire nuts in a roof j-box required to be waterpoof? Trying to find a code section specifically referencing this but no luck so far.
The wet location connectors are required for enclosures or raceways installed underground.

300.50(B) Wet Locations.
The interior of enclosures or raceways installed underground shall be considered to be a wet location. Insulated conductors and cables installed in these enclosures or raceways in underground installations shall be listed for use in wet locations and shall comply with 310.10(C). Any connections or splices in an underground installation shall be approved for wet locations.
 