Res Disconnect next to Panel: is it a subpanel then?
newservice
Syracuse NY
Electrician extraordinaire
Have come across this before, a separate enclosed knife disco for the service, right next to the panel, maybe a foot at most, and panel is fed with 3 wires from the disco not 4, but bonded with a good #4 copper. Panel does not have separated neutrals and grounds as a sub panel would.
Even though separate enclosures,, would you let this fly?
With no OCPD, it is not the 1st means of disconnect w/OCP. So the panel would be your service disconnect and would not be a subpanel.
OK thanks, I did not know that. Makes sense. Even more so if you consider pulling the meter could be a disconnect. Thx!
Take a look at 230.91. It substantiates what Bill states. The disconnect along with the ovecurrent device immediately adajacednt to the disconenct become the service disconnect.
right, I think I did know that but I saw it yesterday and am in a bit of brain fog atm. This reinforces it and points to the code.
I don't agree with my fellow moderators on this. The knife switch is the service disconnect and the bonding must be at the switch. There is nothing that says the service OCPD has to be part of the service disconnect. I see the cited section, 230.91, as supporting my comment.
I'm confused by " fed with 3 wires from the disco not 4, but ]bonded with a good #4 copper." Sounds like 4 wires after all, unless you are describing a bare neutral.
I can't say we are in disagreement (my wording, as always, could have been better). I was attempting to say that I see no problem with the installation as the OCP is immediately adjacent.
I guess I also have Augieitis! :) The main point I was attempting to make was that the panel was not a subpanel.
And I am saying it is a subpanel and requires the ungrounded conductor, the grounded conductor and the grounding conductor between the knife switch and the panel.
I don't see it that way. I think if the code meant it that way, they would have said it. IMO, it's just giving permission to have the OCP to be adjacent to, rather than a part of, the disconnecting means, in effect, making them as one in the same.
I read it the other way. Maybe I will put this on my 2026 PI list.