kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
Minimum GEC is sized per ungrounded service conductor size, regardless of load calculation or overcurrent protection. Just because you "essentially have" 600 amps doesn't mean you can't have 800 amps worth of conductor because someone decided to increase because of voltage drop - which makes that 600 figure irrelevant when sizing the GEC.Thank you for clearing that up for me. I thought it was based upon available amps running inside the home. But it’s available amps running to the home.
Load calcs came in at 570 amps so essentially 600....
Idk if the water service is metal pipe underground between the shutoff and the meter. I’ve seen them use pex for this before. I’m pretty certain the plumber ran 1” rolled copper between the main house and the pool house (50ft) does this qualify GEC at that shut off? Sounds like it may, pool house is a 125amp sub off one of the 200s
So the gas I assume is considered metal throughout despite it not being typical cast iron, they ran a flexible trunk line that wasn’t the typical yellow it was black....
Sent from my iPhone using Tapatalk
If you can't determine whether the incoming water is metallic or not, I'd at very least connect to the known copper line - it still is a qualifying electrode. If main line is metallic as it exits the building the chances are pretty good it is a qualifying electrode also, how often do they replace an old line with non metallic but connect to existing within 10 feet of entry? If it runs below floor before entering maybe, if it enters a basement wall, they pretty much always replace the entire line to and usually including the first shutoff valve.