I am wondering if this installation would be up to code
Present equipment
-Meter outside connected to Florida Power & light.
-200 A disconnect, outside connected to meter.
-200 A Panel connected, inside connected to disconnect.
Proposed work
-Connect a 50 A fusible pull-out disconnect to the side of the 200 A disconnect that is connected to the house panel, and from here putting an L14-30 R receptacle for the generator.
The installer claims that is correct because turning the main breaker off would disconnect comercial power and turning the pull out disconnect on would connect the generator to the house panel without risk of energizing out side the house (since the main breaker would be off).
My Issues with this installation are:
1) He plants to put the 3/0 wire that feeds the house panel and the #8 wire from the generator together in the single lug of the main breaker. I'm pretty sure he can't do that. What can he do to make this connection legally.
2) the plug for the generator is a 30 A why is the pull out disconnect fused at 50 A? that's a bit more than 120%
Please any suggestions would be greatly appreciated, Hurricane season is Here.
Present equipment
-Meter outside connected to Florida Power & light.
-200 A disconnect, outside connected to meter.
-200 A Panel connected, inside connected to disconnect.
Proposed work
-Connect a 50 A fusible pull-out disconnect to the side of the 200 A disconnect that is connected to the house panel, and from here putting an L14-30 R receptacle for the generator.
The installer claims that is correct because turning the main breaker off would disconnect comercial power and turning the pull out disconnect on would connect the generator to the house panel without risk of energizing out side the house (since the main breaker would be off).
My Issues with this installation are:
1) He plants to put the 3/0 wire that feeds the house panel and the #8 wire from the generator together in the single lug of the main breaker. I'm pretty sure he can't do that. What can he do to make this connection legally.
2) the plug for the generator is a 30 A why is the pull out disconnect fused at 50 A? that's a bit more than 120%
Please any suggestions would be greatly appreciated, Hurricane season is Here.