Dennis Alwon said:It is a good thought though--- I may start using the fan rated box. It may eliminate issues later.
And give up all those service calls? :grin:
BTW... love the new avatar...
Dennis Alwon said:It is a good thought though--- I may start using the fan rated box. It may eliminate issues later.
Dennis Alwon said:I rarely use a fan rated box. I always brace the standard octagon with a 2x6 flat across the joist and then screw the bracket into the wood. Surely you don't mean to suggest that is not legal.
Wiring a CF to a smoke circuit as a violation....do you have an NEC article in mind?rosebud said:The installer (often the H/O or a handyman) with hot wire the fan to any j-box they can find including the fire/smoke detector circuit. This is what I mantain is improper.
Why did the room have no switch in the first place?rosebud said:I am site the job as improperly installed due to the lack of the wall (line) switch in the room. Thank you to all who respond to this thread.
A fan box is NOT a requirement - independant support is a requirement:rosebud said:Yes that is correct I am telling H/O's (home owners) that a Fan Box is a NEC requirement.
As discussed previously, there are OTHER methods than just using a "rated" box - thru bolting.314.27(D) Boxes at Ceiling-Suspended (Paddle) Fan Outlets.
Where a box is used as the sole support of a ceiling-suspended (paddle) fan, the box shall be listed for the application and for the weight of the fan to be supported. The installation shall comply with 422.18.
What is your role in all this?rosebud said:We find that many home owners will remove a ceiling light fixture and install a ceiling fan w/ light kit in it place. We have seen many cases were the ceiling fan has pulled the origninal j-box and wiring out of the ceiling. This coupled with the fact that many H/O's are installing the newer remote control fan with out a "line switch" i.e. they will wire them hot to the nearest source of power is a real problem that we are seeing in the many homes that we go into. As an added note we see this happen in homes that were recently sold as an incentive up grade to potential buyers.
rosebud said:Yes that is correct I am telling H/O's (home owners) that a Fan Box is a NEC requirement.
iwire said:So your lying to the H/Os.
Only if it applies w/o "exception"M. D. said:Stretching the truth more like it,.... 314.27(d) if I can give an article number isn't it a code article???![]()
If the box is NOT being used as the sole support...."a Fan Box is a NEC requirement" becomes void - just use a lag bolt314.27 (D) Boxes at Ceiling-Suspended (Paddle) Fan Outlets.
Where a box is used as the sole support of a ceiling-suspended (paddle) fan, the box shall be listed for the application and for the weight of the fan to be supported. The installation shall comply with 422.18.
M. D. said:.... the box will have to be listed for the sole support of a paddle fan even if there is no fan .
That's just what I was thinking. Irrespective of proper support, how do you tell a homeowner, who lives in a house where there is K & T with plaster and wood lath construction, you need chop through the ceiling and down the wall in order to have a switched disconnect means or else they can't mount a paddle fan ? The Rehab Code comes in handy for things like this.celtic said:Why did the room have no switch in the first place?
Wouldn't there be, at a minimum, a switched outlet?
If these installations are in NJ, it would not even raise an eyebrow with our very handy Rehab Code.
goldstar said:That's just what I was thinking. Irrespective of proper support, how do you tell a homeowner, who lives in a house where there is K & T with plaster and wood lath construction, you need chop through the ceiling and down the wall in order to have a switched disconnect means or else they can't mount a paddle fan ?
tallguy said:Apparently you don't need to, at least according to Charlie (I don't have access to the new code myself, so I'm taking his word for it).... see post #13