That is what I been trying to emphasize with most my replies in this thread.Second building or other structures supplied by a feeder have required both an EGC run with the feeder and a grounding electrode conductor connecting the EGC to a grounding electrode at the second building or structure. They are not separate grounding systems as the feeder EGC is connected to the main building grounding electrode system via the main bonding jumper.
Also the connection to earth does not keep points at ground potential. Typically there is a voltage on the neutral as a result of various voltage drops, and all that happens when you connect that to a grounding electrode is that the voltage of the earth is raised, in a small area around the grounding electrode, to match the voltage on the neutral.
NEC needs to step up and come up with better solution then they have for these applications. Swimming pools and equipotential bonding required in those applications is good, but is impractical in large bodies of water. Some sort of method of isolating the system that supplies the dock would be better and still having ground fault protection on some level would enhance it even more. Ungrounded systems could maybe work, capacitance could maybe present problems though which is one advantage of still having grounded system, but need to find a way to isolate it from the regular premises grounding network. Easier said if dock is remote from rest of the regular premises but if you have building pretty much right close to the water it may get more complicated at assuring you keep things isolated.