curt swartz
- San Jose, CA
- Electrical Contractor
PG&E's detail on enclosures (Green Book 5.4.2) only concerns the meter itself. If the OP's enclosure contained only the meter itself, and not any OCPD, then there would be no NEC problem. The main panel always has to meet NEC clearances, regardless of what PG&E has to say on the matter. So when you are using a meter main, you have to comply with both.
In the OP, if the raised door were replaced with a regular 80" x 32" wide door, that would satisfy the NEC clearances, yes? Assuming there are no obstacles below the panel that we can't see, or that they are relocated.
Cheers, Wayne
PG&E require the service disconnect with the meter so you would never have a meter socket only with remote disconnect.