For a residential range that is rated at 9.5kW at 208 single phase, can I go to 220.19 and use 8kW for the demand? The manufacturer recommends 40 amp breaker. At 9kW I'm looking at 43.3A which would be more than the breaker rating. Even at 8kW I'm looking at 38.5A. Will the 40A breaker be ok?