Hey all, thank you in advance for your consideration and feedback on this. I’m pretty sure I’ve covered all the necessary codes, but just in case I wanted to post this here in case anyone sees something off.
Residential project; sizing main feeders and pathway.
I have 2x 125A main panels that are installed approx 60’ from the meters and disconnects. For pathway I have an existing 1.5” pvc conduit that is empty. According to my research, I would be able to pull 6x #2 and 1x #6 within this pathway to service both main panels. My theory is based on the following:
-Main panel feeder can be sized to 83% of the total load; for 125A, 83% is 103.75A
-Derating for 6 current carrying conductors reduces the ampacity of #2 wire by 80%, 130A (90 degree wire) is good for 104A after derating
-Conduit fill calcs out to 39.86%
while I know some of these are right on the line, I don’t have the option to run a second pipe, but this should all work, correct?
thank you!
Residential project; sizing main feeders and pathway.
I have 2x 125A main panels that are installed approx 60’ from the meters and disconnects. For pathway I have an existing 1.5” pvc conduit that is empty. According to my research, I would be able to pull 6x #2 and 1x #6 within this pathway to service both main panels. My theory is based on the following: