- Location
- Connecticut
- Occupation
- Engineer
If I understand your layout correctly, the meters/disconnects are located at a separate structure. The main bonding jumper connection would be made at the disconnects. A grounding electrode conductor should also be connected there.the primary GRC is going to be 2 local ground rods at the main panels. The #6 is just to satisfy the ‘GRC within a pathway.’
There would need to be a grounding electrode system at each dwelling unit as well, connected to the equipment grounding at each panel, but not to the grounded (neutral) conductor.)