Residential Garage Receptacle Wiring

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
The garage requirments seem to change every code cycle. The CMP just can't seem to get this right. Why they allow an outdoor receptacle on the circuit but not a few lights is beyond me.
And it shouldn't really have much to do with EV charging either, if it does they don't have that realistic view of what charging needs can be or are just trying to ease some requirements in over time?
 

SSDriver

Senior Member
Location
California
Occupation
Electrician
I know, but should it be? It’s a debate at we have gone over, just like should one be on a refrigerator or a freezer, it’s hardly never be unplugged


Sent from my iPhone using Tapatalk
Came across this today while doing a panel upgrade and trying to identify circuits. They plug the table saw into it and other tools. 20220503_142119.jpg
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
I know, but should it be? It’s a debate at we have gone over, just like should one be on a refrigerator or a freezer, it’s hardly never be unplugged


Sent from my iPhone using Tapatalk
I thought that GFCI protection is only needed if the receptacles are accessible from the ground level ?
 

groomsey

Member
I always run the opener(s) on its own circuit. I did service on garage doors and had many calls that their opener did not work, go out there and the GFCI in the garage was tripped.


Sent from my iPhone using Tapatalk
On that end, the receptacle would need to be gfci protected anyways due to being in a garage
 

kwired

Electron manager
Location
NE Nebraska
I thought that GFCI protection is only needed if the receptacles are accessible from the ground level ?
210.8 A and B both say "all ...... receptacles ...... installed in ....." with no mention of height or behind obstructions within said spaces.

Before about 2005 NEC there used to be some specific exemptions or allowances like a single receptacle in said spaces dedicated to a specific appliance but at that time they removed all of them. And the picture in post 22 is kind of a part of the reason why. I remember installing a single receptacle in unfinished basement mechanical room for a central vacuum unit not on a GFCI because it was permitted at the time. Come back few months later for some other thing and noticed they did about the same thing as pictured in post 22.
 