I do not believe he is correct. Every where else in the code considers a detached garage part of the dwelling unit. Why would 334 be any different? What is the difference between an attached and detached garage? Just for info. I did get an informal opinion from the NFPA on this years ago and they consider any structures associated with a dwelling unit to be part of that dwelling unit. (within reason of course) This would also apply to apartment complexes. The NFPA opinion would allow the clubhouse of the apartment unit to be wired in NM cable without the 15 minute finish rating.
so i guess the garage would have to be attached in order to use nm cable
I would consider a detached garage as an accessory building to a dwelling unit and apply 334.10(A) which permits NM cable to be exposed in normally dry locations.
I would consider a detached garage as an accessory building to a dwelling unit and apply 334.10(A) which permits NM cable to be exposed in normally dry locations. This will raise the question of protection against physical damage as found in 300.4. Subsection (A) of 300.4 seems to imply that cables run through framing members with not portion of the cable closer to the nearest edge at less than 1 1/4" is protected from physical damage. I think this arguement will go on for ever along with ground lug up or down. This is how I would inspect in this area of Indiana but am looking forward to others responces.
I would consider a detached garage as an accessory building to a dwelling unit and apply 334.10(A)
a local inspector is requiring we wire a unattached open framed residential garage with mc cable instead of nm cable and only siting article 334 as the reason. Is this correct?
mhayes, it would be helpful to know your location. I very recently ( like a couple of minutes ago) learned that NJ has amended 334.10(1) to include the words "and accessory buildings or structures".
you could just add provisions to cook and sleep