Eddie_T
Member
- Occupation
- PE (retired)
Parkway has some interesting adapter cords . . . https://www.parkworld.us/generator-adapter-cord-c12.html?page=2
Good luck powering up a full-size water heater with that, most of which consume 4500 watts.I would like a smaller (4000 watts) ... generator ... for well pump and water heater. ...
Read the fine print in the instruction manual. If you buy two generators, read both instruction manuals.I wonder if with inverters one could sync them using 2 units for 240v (would negate any inverter savings).
Good points! I hadn't checked my water heater requirements, it is 4500 watts so I am stuck with my 5000 watt generator. It just that most of the time I don't need near that much capacity. Synchronized generators are just parallel output for more wattage, not to achieve 240 volts. A better approach for me might be to get the smallest feasible inverter generator for steady loads (TV and lighting) and and just use the 5000 watt generator intermittently for pump and water heater, but not simultaneously. Refrigerator and freezer could probably run off a smaller generator (just not simultaneously).
I'll probably just continue with the 5000 watt Coleman Powermate as outages are only 1 or 2 per year. When it expires I may do the 4000 watt 120v inverter generator and use a 3000 or 5000 watt step-up auto-transformer to supply 240v to the panel. With load shedding and forgetting the water heater it should work out OK. An auto- transformer would eliminate any concern about load balancing as well.
Thanks, I never thought of that approach.I cannot think of a code compliant way to accomplish it, but I have 2 friends with back-woods cabins who have their small 240V water heaters wired to 120V. They heat slowly (1/4 power) but for short showers and hand washing, do fine.
Dedicated transfer switch for the water heater that either connects it to the two ungrounded conductors from the panel, (240v) or one ungrounded and one grounded conductor from the generator, (120v) and never allows the generator conductors to be connected to the panel conductors.I cannot think of a code compliant way to accomplish it ...
Top of the list: Either install a transfer switch (manual or automatic) or tell the client to plan on using a couple extension cords to power specific items. Under no circumstances allow the generator to be connected directly to the house power system (e.g., by plugging it into the dryer outlet). I know someone who used that method to connect the generator of his RV to his house during power outages. I could not talk him out of it. In his case, nothing bad ever happened. That means luck was involved: not his good luck but the good luck of the linemen working to restore power.
I would start asking questions. Examples:
- Are there specific items they wish to have power during a utility outage?
- Do they want the generator to start and take load automatically?
- Pertaining to question 2, what if the utility outage happens when they are not at home (i.e., either at work or on vacation)?
- For an extended outage, will they leave the generator running all night, or will they restart it each morning?
- Also for an extended outage, how will they make sure they have enough fuel to keep the generator going?
- Pertaining to question 5, is natural gas an option for the generator fuel?