Yep, some POCO's are clueless.The POCO up here does not want a ground in the meter base, we bond it, but no ground wire in the can
Sent from my iPhone using Tapatalk
Roger
Yep, some POCO's are clueless.The POCO up here does not want a ground in the meter base, we bond it, but no ground wire in the can
Sent from my iPhone using Tapatalk
If the panelboard has any knockouts above or even with any of the busbars, weathertight gasketed locknuts should be usedI've seen the results of that myself many times and typically try to avoid doing it as well.
Had one last summer that was probably ~30 year or better installation. You probably know NPPD hasn't and still doesn't necessarily put weatherheads on their end of underground laterals that originate at top of a pole. This was one that likely was that way when initially installed, but a second structure to be supplied was added at some time and they just moved the meter to the pole, with a meter/main assembly, but never put a weatherhead on the top of the conduit. Surprised that main breaker lasted as long as it did, especially with aluminum wire in it. We replaced the breaker and had a weatherhead put on the conduit.
Yes, but that still doesn't stop condensation within the raceway, and it will happen in most areas, from draining onto your main lugs/main breaker when it is directly above them.If the panelboard has any knockouts above or even with any of the busbars, weathertight gasketed locknuts should be used
Still straight threads. They leak. Pipe dope.But wait... An offset nipple is not allowed? I had no idea. I've used many of them for that purpose.
Come to think of it, most of mine have been plastic PVC.
The issue is not the offset nipple itself but rather the threads. A PVC offset has the same issue. Offset nipples, PVC MAs, EMT connectors, etc. all have straight threads that are only listed for use with lock nuts.But wait... An offset nipple is not allowed? I had no idea. I've used many of them for that purpose.
Come to think of it, most of mine have been plastic PVC.
No. As I stated in previous post, a PVC MA is only listed to use with lock nuts. The only thing you can use with a threaded hub would be threaded IMC or RGCI don't want to take away from the OPs topic. But it's kind of important. So if I use a straight PVC connector in a hub, it's okay? But not an offset nipple?
Are you telling me that when I have a female and male adapters but no couplings, I can't screw, glue and be done?No. As I stated in previous post, a PVC MA is only listed to use with lock nuts. The only thing you can use with a threaded hub would be threaded IMC or RGC
Don't shoot me, I'm just the piano player.Are you telling me that when I have a female and male adapters but no couplings, I can't screw, glue and be done?
Drummers are usually safe, piano players, I don't know.Don't shoot me, I'm just the piano player.
I don't think there were drummers when that phrase was coined.Drummers are usually safe, piano players, I don't know.
I don't think there were drummers when that phrase was coined.
All threads (factory and field cut) on RMC and IMC are tapered. The threads on an electrical coupling are straight.Arent factory threads on rigid straight threads too? Seems like the coupling goes all the way on those. I know most threading machines are set for tapered threads, so if you cut the conduit and thread it may be a tapered pipe thread.
Does this mean you cant use a factory rigid thread in a hub?