Residential hood with makeup air

Status
Not open for further replies.

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
I've been asked to install, vent, and wire a residential hood that's 1,200 cfm. I know I need a makeup air, too.

I've never wired a redidential makeup air unit.
I have no specs or cut sheet for the hood, so I'm curious what's typical for connecting the MUA to the hood. Is it a particular hood type, with auxiliary power out for MUA?

Maybe similar to a downdraft vent that has remote blower getting powered from main unit?
 
I should add:

This is a rough in on a gutted kitchen. So at this point it's just ducting and wiring. The contractor has not picked out a hood yet, but homeowner wants 1,000+ cfm so I know it needs MUA
 
I should add:

This is a rough in on a gutted kitchen. So at this point it's just ducting and wiring. The contractor has not picked out a hood yet, but homeowner wants 1,000+ cfm so I know it needs MUA
I don't know, most commercial units is just a hood - motor is in separate unit on the outside of the building/on the roof, and you will have a control (possibly just a toggle switch) somewhere inside, in that case just power the MUA from same switch either directly or via a relay if separate circuit is needed.
 
Usually the hvac guy handles the low voltage control from the hood to the blower located remotely or above the hood.
 
I don't know, most commercial units is just a hood - motor is in separate unit on the outside of the building/on the roof, and you will have a control (possibly just a toggle switch) somewhere inside, in that case just power the MUA from same switch either directly or via a relay if separate circuit is needed.
I'm just guessing since it's a residential hood, it probably has the controls on the unit But maybe not
 
I'm just guessing since it's a residential hood, it probably has the controls on the unit But maybe not
I've never seen a resi hood that gives you anything to make this easy. Make up air for resi hoods has been in the ICC for a long time yet the manufacturers act like they have never heard of it.
 
I'm just guessing since it's a residential hood, it probably has the controls on the unit But maybe not
I don't think I ever seen a residential hood with that much CFM. Would think if it were that much might possibly be more like you would find in commercial application. Unless you regularly cooking for 10+ people, who needs that much of a cooking fan in a house?
 
We run into it on almost all of the large homes that we do. There is a air flow switch that is low voltage that goes back to the furnace blower (I have seen that) or to a separate fan and relay
 
When I have had make air on resi hoods I have used a RIB current switch located in the hood to trigger the make up air fan. That way you don't modify any factory wiring.
I just noticed this reply. Thanks

Something like this one?

 
I don't think I ever seen a residential hood with that much CFM. Would think if it were that much might possibly be more like you would find in commercial application. Unless you regularly cooking for 10+ people, who needs that much of a cooking fan in a house?
I've had issue with a simple stock residential hood, the home was very well sealed with insulation and whenever exhaust hood was run or even the dryer it would create enough vacuum to snuff out the pilot on the water heater and the oil furnace would fault out because of it. Had to install a simple actuated baffle that would open to allow for makeup air when heat was running, it worked from the heating unit not the exhaust hood. I know not quite the same thing, but goes to show the residential hood can create enough vacuum to be an issue.
 
I've been asked to install, vent, and wire a residential hood that's 1,200 cfm. I know I need a makeup air, too.

I've never wired a redidential makeup air unit.
I have no specs or cut sheet for the hood, so I'm curious what's typical for connecting the MUA to the hood. Is it a particular hood type, with auxiliary power out for MUA?

Maybe similar to a downdraft vent that has remote blower getting powered from main unit?
I'd tell them you can not pre-wire or vent for an unknown system, and they need to choose one now.
 
I've had issue with a simple stock residential hood, the home was very well sealed with insulation and whenever exhaust hood was run or even the dryer it would create enough vacuum to snuff out the pilot on the water heater and the oil furnace would fault out because of it. Had to install a simple actuated baffle that would open to allow for makeup air when heat was running, it worked from the heating unit not the exhaust hood. I know not quite the same thing, but goes to show the residential hood can create enough vacuum to be an issue.
Commercial building usually bring in outside air to create a positive internal pressure.

A heat-recovery device would be the best way to do that in a home, or at least a vent to the return.
 
I don't think I ever seen a residential hood with that much CFM. Would think if it were that much might possibly be more like you would find in commercial application. Unless you regularly cooking for 10+ people, who needs that much of a cooking fan in a house?

It depends on the BTUs of the gas cooking appliances. It's common today for kitchens to have at least 6 burner ranges, double ovens, griddle, grill, etc. A 1000+ Cfm vent hood with makeup air is not at all unusual. This should be designed by an HVAC guy with credentials in air balancing and ventillation, not the EC or GC.

-Hal
 
I'd tell them you can not pre-wire or vent for an unknown system, and they need to choose one now.

Yeh, that’s the answer. You could try to wire for all the variables, but it’s cheaper if they’ll just make a decision now.


Sent from my iPad using Tapatalk
 
I got some model numbers for hood and makeup air, which is just a damper - not a motor.

Hood:

MUA:

Looks like a 24v damper with air pressure switch. Broan has a calculator/recommendation page to match MUA with hood CFM.

This is likely the setup @Dennis Alwon had in mind. So looks to be pretty straightforward. I'll see what the transformer looks like, and determine where to place it and power it.
 
When I have had make air on resi hoods I have used a RIB current switch located in the hood to trigger the make up air fan. That way you don't modify any factory wiring.
onna deez??>>>

~RJ~
 