stickboy1375 said:The best thing I ever saw was "addict lights"
tallgirl said:What's the maximum permissible continuous load? 16A on a 20A circuit, 12A on a 15A circuit.
iwire said:Julie the maximum possible load on that mixed use circuit is 20 and 15 respectively.
So if that maximum load is expected for more then 3 hours it will then be a continuous load and you may have to rework the circuit.
In no case shall the load exceed the branch-circuit ampere rating. An individual branch circuit shall be permitted to supply any load for which it is rated. A branch circuit supplying two or more outlets or receptacles shall supply only the loads specified according to its size as specified in 210.23(A) through (D) and as summarized in 210.24 and Table 210.24.
tallgirl said:Any house containing "teenagers" should be assumed to have all lighting loads be "continuous" loads.
I do not see the distinction you're trying to make with that statement.tallgirl said:I think you're forgetting that the title of 210.23 is "Permissible Loads", not "Possible Loads".
Are you saying if the circuit happens to be a 15A GPBC then suddenly the 'possible load' is going to change?tallgirl said:The maximum possible load is .8 * 20A * # of receptacles. See 210.23 (A) (1).
georgestolz said:I do not see the distinction you're trying to make with that statement.
Are you saying if the circuit happens to be a 15A GPBC then suddenly the 'possible load' is going to change?
210.23(A)(1) is requiring manufacturers of appliances to limit their appliance to 80% of the circuit it's expected to be connected to, IMO. So an appliance primarily designed for use in the kitchen or the bathroom would be limited to 80% of a 20A circuit (210.11(C)), and appliances for use in other areas of the home would be limited to 80% of a 15A circuit (hence the abundance of 12A vacuum cleaners, for example.)
Edit to add: The speculation in this thread about teenagers leaving lights on, elaborate entertainment systems in bedrooms and so forth really says to me that the NEC should continue to keep their hands out of the design of circuits in the home, IMO. Carried to the ultimate conclusion of that train of thought, each receptacle in the house would need to be a dedicated circuit for "what-if's", and lighting would have to be based on the highest lamp wattage concievably screwed into a luminaire, as opposed to what it's listed maximum would be. :roll:
georgestolz said:I have two triple-taps in my bag, a six-outlet tap in my living room, and a spare sitting on my desk in my office - where does that figure in with your "possible load" bit? I still don't understand what you're getting at.
The "possible load" on an individual branch circuit with a duplex attached is a million gazillion amps. The technology exists to add to the system with extension cords infinitely.