residential load calc help

Status
Not open for further replies.

nizak

Senior Member
I'm looking at adding a pool heater, pool pump, and outdoor jacuzzi type tub to an existing single family residence. Can these items be figured as fastened in place appliances? One load calc form I used had these going in as such, the other listed them seperatetly, and did not afford the benefit of deration. There was a big difference between the total load on the two calcs. Thanks.
 

nizak

Senior Member
One load calc had them being put in the fastened in place appliances section, that gave you a derated number to use in your total calculation. The other one I used just had them listed individually and their values were 100%. If in fact they are to be figured as F.I. P. appliances then I can figure it per NEC.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
I did some looking and thinking. I think the pool heater should be a FIPA, the pump is a motor 125% largest, 100% others), and the jacuzzi tub is a FIPA, IMO.
 

cadpoint

Senior Member
Location
Durham, NC
Since your stating in a house in three places in 220.82(B), 220.83(A) & (B) - (all happen to be) 3a, they all say a specific circuit...
 